0.5 L Hydraulic pump spec discrepancy
|
07-26-16, 01:34 PM
Post: #23
|
|||
|
|||
RE: 0.5 L Hydraulic pump spec discrepancy
Scoffer,
The other thread which you have mentioned did not include any additional pertinent detail and will be deleted accordingly. While this thread is no diverging from it's original subject, we'll finish the discussion here. As indicated previously, sensed motion motion of the vessel is a critical part of the operation of this autopilot. Rather than speculate that something may be wrong, you may want to perform the drive motor test specified previously (i.e. motor lead momentarily connected directly to a 12VDC source). If the pump does not perform properly during the test, then create a new thread to discuss the pump problem. However, should the test not identify a problem with the pump, then the vessel should be taken out to permit it to determine the vessels handling characteristics and determine the deviation fields sensed by the EV-1 Sensor Core. |
|||